Q.
In a marriage hall, there are 15 bulbs of 45W,15 bulbs of 100W,15 small fans of 10W and 2 heaters of 1kW. If the voltage of the electric main is 220V, then the minimum fuse capacity (in A ) of the building should be
Total power is given by, sum of power of all the electrical components, i.e. Ptotal=P1+P2+P3+P4 , where P1,P2,P3,P4 represents power of 45W bulb, power of 100W bulb, power of small fan and power of heater respectively. ⇒Ptotal=(15×45)+(15×100)+(15×10)+(2×1000)=4325W
So current is =2204325=19.66A≈20A